Do all fire alarm devices need need to be Verified?
-
- Posts: 14
- Joined: Tue Sep 03, 2013 4:36
Do all fire alarm devices need need to be Verified?
Hi,
Will be replacing CPU, all modules, power supply and batteries inside fire alarm panel due to water damage.
This is a 12 story building, with 150 units. When conducting V.I. do all devices for in suites and common area require testing, or can I test one device per circuit, per floor.
Thanks.
Will be replacing CPU, all modules, power supply and batteries inside fire alarm panel due to water damage.
This is a 12 story building, with 150 units. When conducting V.I. do all devices for in suites and common area require testing, or can I test one device per circuit, per floor.
Thanks.
-
- Site Admin
- Posts: 71
- Joined: Sat Aug 23, 2008 9:10
- Location: Vancouver, B. C., Canada
- Contact:
Re: Do all devices need V.I
Your job falls under Section 6 of the Standard for Verification of Fire Alarm Systems. Clause 6.8 states:
"Where an existing fire alarm system control unit or transponder is replaced with a new control unit or transponder, it shall be verified in accordance with Subsection 4, Control Units and Transponders, and any existing devices shall be tested in accordance with Section 5.7 (Field Devices) of CAN/ULC-S536, Standard for Inspection and Testing of Fire Alarm Systems. (Refer also to Clause 6.11)"
Clause 6.11 states:
"Software modifications shall be tested by one of the following methods:
A Reverifying all system functions that could be affected by the modifications with the exception of wiring supervision; or
B A comparison of the 'before' and 'after' software utilizing mediums such as a printout or compare program."
I included Clause 6.11 even though your question clearly is answered by Clause 6.8 because of the reference to it. You will have to drop the end-of-lines. I'd suggest you document the voltage readings for each one on the remarks line of the Individual Device Test Record. This will ensure that the wiring hasn't been adversely affected between the common control and the last device in the circuit.
Do you have the panel manual? If not, email me and I'll see if I can send you the PDF. tech@firetechs.net
"Where an existing fire alarm system control unit or transponder is replaced with a new control unit or transponder, it shall be verified in accordance with Subsection 4, Control Units and Transponders, and any existing devices shall be tested in accordance with Section 5.7 (Field Devices) of CAN/ULC-S536, Standard for Inspection and Testing of Fire Alarm Systems. (Refer also to Clause 6.11)"
Clause 6.11 states:
"Software modifications shall be tested by one of the following methods:
A Reverifying all system functions that could be affected by the modifications with the exception of wiring supervision; or
B A comparison of the 'before' and 'after' software utilizing mediums such as a printout or compare program."
I included Clause 6.11 even though your question clearly is answered by Clause 6.8 because of the reference to it. You will have to drop the end-of-lines. I'd suggest you document the voltage readings for each one on the remarks line of the Individual Device Test Record. This will ensure that the wiring hasn't been adversely affected between the common control and the last device in the circuit.
Do you have the panel manual? If not, email me and I'll see if I can send you the PDF. tech@firetechs.net
-
- Posts: 14
- Joined: Tue Sep 03, 2013 4:36
Re: Do all devices need V.I
Hi,
Yes I do have the panel manual. Thank you for your help and knowledge.
Yes I do have the panel manual. Thank you for your help and knowledge.
-
- Site Admin
- Posts: 71
- Joined: Sat Aug 23, 2008 9:10
- Location: Vancouver, B. C., Canada
- Contact:
Re: Do all devices need V.I
You're most welcome. Feel free to join our new LinkedIN forum. Your question is going to be posted as a FAQ on the Verification section, so thank YOU! ![Smile :-)](./images/smilies/icon_e_smile.gif)
![Smile :-)](./images/smilies/icon_e_smile.gif)