Hello,
When testing duct smoke detectors inside a furnace does it have to shut down on alarm.
The testing is done on a row of 25 townhouses. Each townhouse has 2 bedrooms. Also does the wiring to these devices have to be armored?
Thank you
Duct Smokes
Forum rules
Blatantly advertising your services is strictly prohibited. Violators will be banned from posting. Identification with a company engaged in providing fire equipment service is encouraged in order to validate responses (i.e. a "tag line" which states your name, company's name and contact information is allowed).
Blatantly advertising your services is strictly prohibited. Violators will be banned from posting. Identification with a company engaged in providing fire equipment service is encouraged in order to validate responses (i.e. a "tag line" which states your name, company's name and contact information is allowed).
-
- Site Admin
- Posts: 71
- Joined: Sat Aug 23, 2008 9:10
- Location: Vancouver, B. C., Canada
- Contact:
Re: Duct Smokes
This depends on what the local jurisdictional requirements are. There is a major issue with duct smokes installed in the plenum over a standard forced air furnace. Depending on how CLOSE the assembly is to the heat exchanger, you could easily exceed the maximum temperature rating on the detector. It's rare these devices are ever properly installed as there is no testing parameter for them except for those proscribed in the Standards related to Fire Alarm Systems (in Canada). If there is no "fire alarm system" installed in the building (and you're in Canada), the testing wouldn't apply (and would be difficult to enforce). To my way of thinking, these units should not only shut down the furnace, they should also cause the smoke alarms in the unit to sound as well.
-
- Posts: 14
- Joined: Tue Sep 03, 2013 4:36
Re: Duct Smokes
Thank you for the info.
The duct smoke is about 18'' from the heat exchanger. There is a fire alarm panel that the duct smokes are tied into.
The testing is also in Canada.
Thank you
The duct smoke is about 18'' from the heat exchanger. There is a fire alarm panel that the duct smokes are tied into.
The testing is also in Canada.
Thank you